I looking for a loading guide for distribution transformers. At what point is a transformer overloaded? At nameplate KVA, at 20% over nameplate? How does the seasonal peak factor in? Mfgs tend to recommend not loading beyond the nameplate KVA. What about "degrees C rise"? -- Thanks.
 
Replies continue below

Recommended for you

If it is in the USA and it is not for a Power Utility then you cannot overloads it per NEC. For Power Utilities, check with them for what is acceptable.
 
Actually, in some instances the NEC allows 250% overloading, while IEEE 242 recomends no more than 125%. Personally, I side with the manufacturers and their nameplate ratings and set overcurrent protection at 100% of rating.
 
The transformer and all its accessories are designed to take 150% load for not more than 30minutes.

It is important in case of parallel transformers that one transformer carries the overload when the other trips till such time the load shedding takes place to brings down the load. If the transformer over current protection is not set to take this need in to account, it is likely that the second transformer also trips and no one would like it.

This is a critical requirement in case of grid transformers and many a grid failures are as a result of conservative settings adopted for transformer over current protection.
 
The problem with 150% overload for 30 minutes is that every O/C device available typically has a LT delay of not much more than 10 minutes, and normally this is set for much less for coordination purposes.
Even if you set the LT pickup at 150% so the trip will occur before 10 minutes, then the curve will allow overloads up to 150% (between 100% and 148% or so) for an indefinite time.
The only safe way to protect a transformer is by using the manufacturer's nameplate limits, or use temperature relays to trip out the secondary device when the temperature reaches the nameplate limits.
 
The O/C protection is not meant to protect the transformers against overloads. The temperature measuring devices are equipped to do that job very well and if overload protection is critical, the present day numerical over current protection relays come with an additional element for the purpose.

Trying to protect the transformer against overloads with O/C protection generally we get in to bigger problems and undesirable situations, this is my experience.
 
raghunath is absolutely correct for the type of application he is talking about...utility type systems or engineered systems not falling under NEC or similar codes.

However, if your installatin falls under NEC (in the United States speciallly), you have to follow NEC..

As for the definition, overload will be anything beyond its rating..it is a different matter how much overlaod is tolerable for how long.

Utilities can overload trasnformers for the reasons raghunath gave and also the fact they can afford to..some reduction in life due to repeated overloading is not a concern for them..it may not be the case in your case.

 
I am pretty sure that the NEC does not state transformer sizing requirements anywhere. It does state feeder sizing requirements, and it does state maximum sizing of OC devices for transformers, but it doesn't mandate transformer sizes.

I would consider any load over nameplate rating to be an overload. Whether or not the overload is acceptable is a different question.

For what it's worth -- I will generally size secondary transformer overcurrent protection at 125% of nameplate, which is in accordance with NEC. With 100%-rated breakers, that would permit a 125% overload to exist continuously. No code violation.

As mentioned above, utility requirements are different than us mere mortals. But the utility philosophies can be interesting and enlightening none the less. Around here, our utility wouldn't bat an eye at continuous 10 to 20% transformer overload. And they would not lose much sleep over 40%.

I've heard that it's more cost effective for utilities to replace transformers when they burn out from overload than it is for them to monitor the load and take care of overload situations.

Keep in mind that heat is the real problem that will kill the transformer -- so fans can be helpful in squeezing a bit more power out of a transformer beyond it's actual nameplate rating. Similarly, if you have the transformer stuffed into a 120-degree electrical room, you may find that nameplate IS an overload condition. . . .
 
"I've heard that it's more cost effective for utilities to replace transformers when they burn out from overload than it is for them to monitor the load and take care of overload situations."

That works as an operating philosophy when you have a stock yard with spares. For an owner with just a few transformers the economic picture would be just the opposite.
 
Re my statement "I am pretty sure that the NEC does not state transformer sizing requirements anywhere." -- by the way, I'd love for someone to prove me wrong. I wish the NEC did mandate a minimum transformer size. But, despite looking hard through the NEC for such a requirement, I've never found one.

If anyone thinks the NEC does specify transformer size, please provide a code reference.
 
I think that the closest NEC requirement for minimum transformer sizing is arrived at backwards through the the requirements for maximum transformer overcurrent protection.

There is also NEC 110.3(B) to consider, are the nameplate FLA values "instructions"?
 
Transformers thermal loading beyond nameplate in the US and ANSI marketplace follow the IEEE/ANSI Standard C57. 91 & 92 as primarily guide while Europe and other countries follow the IEC standard 354 & 905 for the same purpose.

Statistics compiled In the pass 30 years by EPRI, IEEE and EEI shows not significant increase in transformer failure rates using the overloading criteria of 3% annual loss of life (ALOL) provided not exceeding the following constrains:

-115 deg C maximum top oil temperature
-160 deg C maximum hot spot temperature (55 deg C insulation)
-180 deg C maximum hot spot temperature (65 deg C insulation)
-LTC switch capability
-Bushing capability
-Insulation moisture content
-Tank oil expansion limits

See the enclose information for aditional reference in this subject:[sub]
[/sub]
 
davidbeach -- no doubt -- I agree with you on that one. But if we size the OC device at 100% of demand load, and the OC device is allowed to be 250% of transformer rating, then that means we could install a transformer sized to handle only 40% (inverse of 250%) of the load it is expected to carry and still be in full compliance with NEC.

That's kind of out of character for the NEC, where most everything else is sized at 100 or 125 or 250% of the load it carries.

And we could actually take that even further. Only the feeders are required to be sized to handle 100% of their demand load. There's no reason that the OC devices need to be sized as large as the feeder ampacity -- they, and their transformer, could be even further reduced in size.
 
peebee - I've never quite understood those rules either, but for any secondary under 600V and over 9A, not in a supervised location, the secondary must be protected at 125%, or the next standard size. Maybe overloaded transformers fail safely, after all, the NEC only claims to provide safety, not practicality. Practicality is why us consulting engineers exist.
 
I think you guys covered this one pretty well. For what it's worth:

1) I also size primary OC at 125% primary current at full nameplate load as a rule of thumb, whether or not I have OC protection on the secondary. (Based on NEC table 450 -3)

2) Any loading above nameplate is definitely an overload condition.

3) Acceptability of any overload that doesn't pop the primary OC protection, in terms of severity or duration, is all determined by temp rise. (don't exceed the nameplate rise rating)

Regards,

NEMA6P

 
I am confused, I have not done much residential utility work, however I am faced presently with removing and re-locating some power poles. A typical case is one transformer supplying three ~2000 sq ft residentials using a single-phase pole-mounted unit transformer. I assume that these are 100A services. So on the conservative side 80*3=240A, and at 240V is 57 Kva. Way-way to big for a typical utility to install. Now using peebees 40% gives me 22.5kva, still looks too high, considering 15kva appears to be what is currently installed. However, since it will be necessary to install new transformers to minimize the outages is there a diversity factor in play here that given peebee's 40% or 2.5*15kva = 60kva or 156A/3 = 52A expected coincident load?
 
I have never done any utility work, but I've worked with plenty of utility engineers and I can guarantee that they will use a much smaller demand factor than we would typically use on the NEC side of things. I can't give you any good rules of thumb on a demand factor to use. But I can give you the following tidbits which might help point you in the right direction:

+ Utilities seem to size their transformers at about 50% to 75% of what we would size them at (which is often based on connected load or 75-80% of connected load).

+ There are quite a few articles out there about the philosophy behind NEMA TP-1 transformers (Energy Star high-efficiency transformers). A lot of research has been performed on transformer loading, and most of it seems to indicate that most small transformers are loaded to something like 30% of nameplate.

You might want to contact some utility engineers and see if they can give you some pointers on transformer sizing (just curious -- GOTWW, are you a utility engineer? If not, how come you're sizing a utility transformer?).

Also, I'd forget about your 80*3=240A starting point for your calculations. I'd think a better bet would be to get some good rule of thumb numbers for w/sf for residential and start there. Unfortunately, I can't give you any guidance there, either, most of my work is in commercial/industrial. But, my guess would be about 3 w/sf. Assuming 3x 2500sf houses, that would be 15 kVA demand. DON'T BASE YOUR DESIGN ON THIS. But this does indicate that your calcs may be high. And maybe someone else can throw out some better w/sf numbers.

Actually, after taking a look at NEC Table 220.3(A), I'm starting to think even 3w/sf might be high for residential for utility purposes. . . .
 
From the good-old westinghouse t&d book, "satisfactory overload protection of a distribution transformer cannot be obtained with a primary fuse, because of the difference in the shape of its current time curve od a distribution transformer......... because of this a primary fuse should be selected on the basis of providing short-circuit protection onlyand its minimum blowing current should usually exceed 200% of the full load current of its associated transformer". It goes on to say that transformer failures to overloads are unusual, with the majority of catistrophic failures are due to high impedance secondary faults, tree limbs etc.

This reminds me of this weekend, and the cascading transformer explosions in florida, probably due to high impedance secondary faults. And of course Mr Heroldo(?sp) explinating the virtues of UG electrical.
 