we have a 2400VAC delta distribution system with 10 single and 12 three phase distribution transformers. the total kva is about 1000, but we only average 57 kw usage. the xfmrs range in age from 30 years to 100 years old. we are billed at 2400VAC with no penalty for power factor. i would like to measure the transformer losses and distribution line losses:
cable resistance losses
cable insulation losses
xfmr primary copper losses
xfmr iron losses
xfmr seconday copper losses
we may conclude that we will save on our electric bill (currently 75,000 annually) by replacing some or all of the xfmrs.
i can estimate the cable resistance losses from the wire gauges.
We do not have very sophisticated test equipment, only an amprobe DM-II for secondary data logging and 4 1200:100 hv current transformers.
since our smallest xfmrs are 5 kva, i expect to need to measure very small currents. i think that 100 windings of hv test wire through a hv ct may work for iron losses with the secondary open.
i think that using the dm II with its cts on loops from the hv cts on the primary side and its voltage probes on the secondary side will give me power factor.
our low ohms tester only puts out 100 ma, so i think we cannot get good test results on four wire tests on the xfmr windings.
any help you can give us on xfmr and cable testing on a low budget will be greatly appreciated.
-thanks
-Craig
cable resistance losses
cable insulation losses
xfmr primary copper losses
xfmr iron losses
xfmr seconday copper losses
we may conclude that we will save on our electric bill (currently 75,000 annually) by replacing some or all of the xfmrs.
i can estimate the cable resistance losses from the wire gauges.
We do not have very sophisticated test equipment, only an amprobe DM-II for secondary data logging and 4 1200:100 hv current transformers.
since our smallest xfmrs are 5 kva, i expect to need to measure very small currents. i think that 100 windings of hv test wire through a hv ct may work for iron losses with the secondary open.
i think that using the dm II with its cts on loops from the hv cts on the primary side and its voltage probes on the secondary side will give me power factor.
our low ohms tester only puts out 100 ma, so i think we cannot get good test results on four wire tests on the xfmr windings.
any help you can give us on xfmr and cable testing on a low budget will be greatly appreciated.
-thanks
-Craig