squeeky
Electrical
- Aug 26, 2013
- 171
Country: Malawi
Soil Type: Sandy.
Earthing network: Tested every year. No problems.
Transformer: Siemens.
Gefol. 2000kVA. 3.3kV to 400v. Dyn11.
MV Cable is PEX. 90 meters.
MV protection: Reyrolle 2DCC IDMTL Fault Level 19.77kA
CT 400:1
θA = 105
θC = 105
Earth = 15
LV MCA breaker Siemens.
Feeding a boiler MCA.
Boiler feed water pump is 250kW, 4 pole. Largest motor in panel. One of two.
Occasionally when the pump #2 is started, as it changes from star to delta, the MV Breaker trips on earth fault.
Motor insulation test shows no faults.
Motor draws normal current.
Star delta starter is wired correctly and has been re-wired.
Earthing has been checked and no errors found. <1 ohm on test to earth mat.
Transformer has been changed.Crack in MV blue phase coil was found.
Protection relay has been changed.
Any ideas?
Soil Type: Sandy.
Earthing network: Tested every year. No problems.
Transformer: Siemens.
Gefol. 2000kVA. 3.3kV to 400v. Dyn11.
MV Cable is PEX. 90 meters.
MV protection: Reyrolle 2DCC IDMTL Fault Level 19.77kA
CT 400:1
θA = 105
θC = 105
Earth = 15
LV MCA breaker Siemens.
Feeding a boiler MCA.
Boiler feed water pump is 250kW, 4 pole. Largest motor in panel. One of two.
Occasionally when the pump #2 is started, as it changes from star to delta, the MV Breaker trips on earth fault.
Motor insulation test shows no faults.
Motor draws normal current.
Star delta starter is wired correctly and has been re-wired.
Earthing has been checked and no errors found. <1 ohm on test to earth mat.
Transformer has been changed.Crack in MV blue phase coil was found.
Protection relay has been changed.
Any ideas?