I'm a little confused about the name plate data on a transformer.
I am trying to find the Nominal KVA and Full Load KVA for a tranformer.
Here is the name plate data:
Westinghouse 4160 - 480Y/277 60 Hz 3 phase
Type RSL Unit Substation Transformer
Class OA
Full Load KVA = 2000/2240
Deg C Rise = 55/65
263 Gal Liquid
Insturction Book = PC 1001
Full Wave Impulse Level HV 60KV LV 30KV
Impedance Level 5.56% at 2000 KVA
4160 to 480y Volts
Ser. No. PBT0297-0103
Mfg. Date 10/1979
My questions are:
The name plate lists Full Load KVA = 2000/2240. Why is there two settings? Which is the Nominal KVA and which is the Full KVA?
Impedance level is 5.56%. How do I calculate the X and R percentage for positive and negative.
There is another transformer with settings: 25/33/42/46MVA. Again, what does it mean and which numbers are Nominal KVA and Full Load KVA.
If the transformer is oil filled and has fans, is it called forced air transformer?
Thank you for your help!
I am trying to find the Nominal KVA and Full Load KVA for a tranformer.
Here is the name plate data:
Westinghouse 4160 - 480Y/277 60 Hz 3 phase
Type RSL Unit Substation Transformer
Class OA
Full Load KVA = 2000/2240
Deg C Rise = 55/65
263 Gal Liquid
Insturction Book = PC 1001
Full Wave Impulse Level HV 60KV LV 30KV
Impedance Level 5.56% at 2000 KVA
4160 to 480y Volts
Ser. No. PBT0297-0103
Mfg. Date 10/1979
My questions are:
The name plate lists Full Load KVA = 2000/2240. Why is there two settings? Which is the Nominal KVA and which is the Full KVA?
Impedance level is 5.56%. How do I calculate the X and R percentage for positive and negative.
There is another transformer with settings: 25/33/42/46MVA. Again, what does it mean and which numbers are Nominal KVA and Full Load KVA.
If the transformer is oil filled and has fans, is it called forced air transformer?
Thank you for your help!