Transformer Nameplate Data 1

Status
Not open for further replies.

shoegoo

Electrical
Nov 15, 2010
1
On a 13200/22860Y x 277/554 single phase transformer, what is the significance of the 554 on the nameplate data? This unit as used on a three phase bank is 277/480 secondary. Any ideas?
 
Replies continue below

Recommended for you

Secondary voltage; either 277 Volts or 554 Volts.
There are two 277 Volt secondary windings that may be internally connected in parallel or in series.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 