sparky_007
Electrical
- Jan 16, 2019
- 7
Hello,
For a transformer 13.8kV WYE-Neutral bushing to NGR (Low Resistance Grounded) cable or 69kV WYE-Neutral to Ground cable (Solidly Grounded) cables, is it shielded or unshielded?
Per NEC/CEC standards, any cable above 2kV should be shielded and by that requirement, neutral cable shall be shielded as well. However, the transformer manufacturer insists on using unshielded cable as the neutral is not a continuously current carrying conductor and will run currents only for 1 or 2 sec before the relay will trip.
Before I push back to vendor to use shielded cable, I wanted to know what others have done in this scenario.
For a transformer 13.8kV WYE-Neutral bushing to NGR (Low Resistance Grounded) cable or 69kV WYE-Neutral to Ground cable (Solidly Grounded) cables, is it shielded or unshielded?
Per NEC/CEC standards, any cable above 2kV should be shielded and by that requirement, neutral cable shall be shielded as well. However, the transformer manufacturer insists on using unshielded cable as the neutral is not a continuously current carrying conductor and will run currents only for 1 or 2 sec before the relay will trip.
Before I push back to vendor to use shielded cable, I wanted to know what others have done in this scenario.