I am recalculating the reach of a dev. 21 generator protection relay. Included in the previous reach of the device was the step-up transformer and 90% of the transmission line. The transformer is a 22.8/345KV 258/430MVA transformer. From the transformer test report, the impedance is 0.1026+4.416j ohms on a 258MVA base.
Looking at the original calculations of the transformer impedance, I am confused by their method. The following is written:
"%Z = 0.1026% + j4.416%(on 258MVA base)
at the 22.8KV terminals:
Zohms=(10*22.8^2 / 258,000)[0.1026 + j4.416]"
I would think that the 22.8KV per unit impedance would be calculated by taking the 345KV impedance, multiplied by (22.8/345)^2 and divided by 258MVA.
Based on my thinking, the Zohms equation above doesn't make sense. If someone understands how that equation works, please let me know. Or is my thinking wrong?
When they calculate the impedance from the transmission line, they do use my thinking. "Ztrans=5.3+j44.5, Z at 22.8KV terminals = (22.8/345)^2*Ztrans = 0.0231+j0.1944"
Looking at the original calculations of the transformer impedance, I am confused by their method. The following is written:
"%Z = 0.1026% + j4.416%(on 258MVA base)
at the 22.8KV terminals:
Zohms=(10*22.8^2 / 258,000)[0.1026 + j4.416]"
I would think that the 22.8KV per unit impedance would be calculated by taking the 345KV impedance, multiplied by (22.8/345)^2 and divided by 258MVA.
Based on my thinking, the Zohms equation above doesn't make sense. If someone understands how that equation works, please let me know. Or is my thinking wrong?
When they calculate the impedance from the transmission line, they do use my thinking. "Ztrans=5.3+j44.5, Z at 22.8KV terminals = (22.8/345)^2*Ztrans = 0.0231+j0.1944"