- May 29, 2003
- 37
My utility started using a #2 Stranded Copper for their loop ground on overhead distribution transformers (versus #6 solid copper previously). I can't figure out the reasoning to this. For a 167kVA 120V transformer the fault current is max 57,300 amps. With this size fault current the short-circuit ampacity of niether the #2 or the #6 would be big enough. However, the ground resistivity is much higher than the resistivity of the ground wire, so it seems like that would be the limiting factor. Therefore, a #6Cu wire would work just as well.
Can anyone enlighten me on the best ground wire size to use?