Transformer overload

Status
Not open for further replies.

thinker

Electrical
Aug 2, 2001
247
When ordering a drive isolation transformer should I specifically request the overload capability 150% for 60 sec, or this overload will be provided anyway based on some general standards transformer manufacturers must follow?
 
Replies continue below

Recommended for you

There is no such thing as a "good measure" when buying transformers.

You get exactly what you specify. If you say 10 kVA - you get 10 kVA. If this is for a frequency inverter you should make sure that the bad power factor (not displacement PF but distortion PF) is taken in account.

A 50 percent overload (i.e. 150 percent load) for 60 seconds is not a problem for a reasonably sized transformer. It has a lot longer time constant - probably in the 15 minutes region, if naturally cooled. Forced cooling will make the time constant considerably lower and you may have a problem with 50%/60 secs overload. But not with a self-cooled one.

If the transformer manufacturer is any good, he will be able to help you out if you explain the application.

Gunnar Englund
 
Thanks, Gunnar. I actually tried to find out whether UL listed transformers (USA) provide this overload as a default (range 200-800 kVA).
 