dpc
Electrical
- Jan 7, 2002
- 8,707
A friend of mine is involved in trying to come up with a power source for an on-site partial discharge test of a very big transformer. One of the requirements is a large shunt reactor on the low side, connected between the test generator (120 Hz) and the transformer LV bushings.
I'd think the transformer would appear as a highly inductive load anyway, so I'm curious about the purpose/need for the shunt reactor?
Anyone familiar with transformer partial discharge test setups?
I'd think the transformer would appear as a highly inductive load anyway, so I'm curious about the purpose/need for the shunt reactor?
Anyone familiar with transformer partial discharge test setups?