Hi All,
I have a customer specification that calls for a test, or in lieu of a test, a calculation to demonstrate the maximum potential between the transformer core and ground during a transient condition based off characteristics of its surge arresters on both the primary and secondary. The transient (unknown value) voltage would be applied to any terminal. The HV side of the transformer is in Y, with the secondary being Y but with a reactance inserted in series between the neutral and the ground.
Just a few questions/pointer requests from my side:
1. Do you have any good reference for the transient model of a transformer so I can model or at least do a rough hand calculation of this?
2. I don't have the electrical model of the transformer, so in parallel with 1, would this be something that I need to ask the manufacturer of the transformer for, or could I make assumptions?
3. Any idea on the purpose of this test? My understanding would be that the core is coupled to the ground permanently via a jumper, so in a practical situation (so long as the jumper/series resistor is not fried) there should be no significant effects.
Thanks!
I have a customer specification that calls for a test, or in lieu of a test, a calculation to demonstrate the maximum potential between the transformer core and ground during a transient condition based off characteristics of its surge arresters on both the primary and secondary. The transient (unknown value) voltage would be applied to any terminal. The HV side of the transformer is in Y, with the secondary being Y but with a reactance inserted in series between the neutral and the ground.
Just a few questions/pointer requests from my side:
1. Do you have any good reference for the transient model of a transformer so I can model or at least do a rough hand calculation of this?
2. I don't have the electrical model of the transformer, so in parallel with 1, would this be something that I need to ask the manufacturer of the transformer for, or could I make assumptions?
3. Any idea on the purpose of this test? My understanding would be that the core is coupled to the ground permanently via a jumper, so in a practical situation (so long as the jumper/series resistor is not fried) there should be no significant effects.
Thanks!