I would like to get opinions from our experienced folks.
On our CEC code, (Rule 8-102): The maximum voltage drops from the supply point up to the feeder bus and from each branch circuit up to the point of utilization shall not exceed 3%. However, the total voltage drop from the supply point up to the point of utilization shall not exceed 5%.
Our designers sizing 600V transformer primary cables from MCCs are sizing them based on a 3% limit. Consequently, the 600V incoming cable from the 4160-600V transformer feeding the MCC is based on a 2% limit. Again, the 4160 cable primary of the upstream transformer is designed based on 3%.
My comment is that 1) The transformer is NOT a utilization equipment, hence, the 3% rule does not apply when sizing it's primary cable. 2) Since the primary current is a direct proportion ot it's secondary current via transformation ratio, the primary cable voltage drop limit should be lesser than the secondary voltage drop limit to allow compensation for voltage drop due to transformer impedance.
Because of this, we always adjust the primary tap changers because load flow studies indicated very low nominal voltage at the secondary (especially to 600-208Y/120V transformers). When I asked them and presented my argument, they told me that the client instructed them to save cable costs and anyways, the transformer taps can be adjusted.
I came to believe that taps are there to obtain flexibility of voltage adjustments in cases when the supply becomes weak due to future load additions. What is happening is that the primary cables are deliberately sized to 3% VD limit with the justification that the taps may be adjusted...I think something is wrong here...can anybody shed light to me if I'm wrong?
On our CEC code, (Rule 8-102): The maximum voltage drops from the supply point up to the feeder bus and from each branch circuit up to the point of utilization shall not exceed 3%. However, the total voltage drop from the supply point up to the point of utilization shall not exceed 5%.
Our designers sizing 600V transformer primary cables from MCCs are sizing them based on a 3% limit. Consequently, the 600V incoming cable from the 4160-600V transformer feeding the MCC is based on a 2% limit. Again, the 4160 cable primary of the upstream transformer is designed based on 3%.
My comment is that 1) The transformer is NOT a utilization equipment, hence, the 3% rule does not apply when sizing it's primary cable. 2) Since the primary current is a direct proportion ot it's secondary current via transformation ratio, the primary cable voltage drop limit should be lesser than the secondary voltage drop limit to allow compensation for voltage drop due to transformer impedance.
Because of this, we always adjust the primary tap changers because load flow studies indicated very low nominal voltage at the secondary (especially to 600-208Y/120V transformers). When I asked them and presented my argument, they told me that the client instructed them to save cable costs and anyways, the transformer taps can be adjusted.
I came to believe that taps are there to obtain flexibility of voltage adjustments in cases when the supply becomes weak due to future load additions. What is happening is that the primary cables are deliberately sized to 3% VD limit with the justification that the taps may be adjusted...I think something is wrong here...can anybody shed light to me if I'm wrong?