timm33333
Electrical
- Apr 14, 2012
- 198
I have a question about sizing the primary fuse for 12.47kV-480V 3750 kVA transformer. The primary full load current would be 174A, and a 200A fuse would be required. For S&C SMU-20 fuses: 100E has a continuous current rating of about 200A, and 200E has a continuous current rating of about 500A. Should the fuse be sized on E-rating or on continuous current rating? In other words, should we select 100E fuse or 200E? Thanks