cuky2000
Electrical
- Aug 18, 2001
- 2,133
We are in process installing a temporary distribution substation with two small power transformers 9/12/15 MVA, Delta/Wye Gnd, 26kV/4.16 kV that will operated temporarily for one year while a new up-rated substation is under construction.
To protect the available temporary old transformer(>30 years in service), primary 34.5 kV fuses had been proposed with the following ratings:
1) Single 300E fuses with single disconnect switch per phase (larger single fuse available)
2) Twin 2-200E fuses and 2-switches per phase.
Some of the issues discuses are:
a) Choose single fuse even if limit the maxi. transformer near the top nameplate rating with limit emergency overloading.
b) Oversize primary fuses to allow the operator to overload the equipment beyond the nameplate capacity under emergency conditions.
Selecting option (a)the equipment could be loaded limited up to 13.5 MVA cont., 15 MVA daily for 1.3 hrs. and 18.4 MVA emergency for 1/2 hrs. Single fuse is also the most cost effective option.
Although, overloading equipment is not an unusual practice in the utility environment with relative new equipment, there is concern overloading >30 years in service equipment and be exposed to unknown risk of catastrophic failure in an active construction site at extra cost using two fuses and switches per phase.
Enclosed is a simplified one line diagram to illustrate this case.
We will appreciate your feedback and comment for this temporary application
Thanks
To protect the available temporary old transformer(>30 years in service), primary 34.5 kV fuses had been proposed with the following ratings:
1) Single 300E fuses with single disconnect switch per phase (larger single fuse available)
2) Twin 2-200E fuses and 2-switches per phase.
Some of the issues discuses are:
a) Choose single fuse even if limit the maxi. transformer near the top nameplate rating with limit emergency overloading.
b) Oversize primary fuses to allow the operator to overload the equipment beyond the nameplate capacity under emergency conditions.
Selecting option (a)the equipment could be loaded limited up to 13.5 MVA cont., 15 MVA daily for 1.3 hrs. and 18.4 MVA emergency for 1/2 hrs. Single fuse is also the most cost effective option.
Although, overloading equipment is not an unusual practice in the utility environment with relative new equipment, there is concern overloading >30 years in service equipment and be exposed to unknown risk of catastrophic failure in an active construction site at extra cost using two fuses and switches per phase.
Enclosed is a simplified one line diagram to illustrate this case.
We will appreciate your feedback and comment for this temporary application