sparkview
Electrical
- Nov 12, 2015
- 59
Hi all,
We are currently installing 4 new station transformer of 1600 kVA each as indicated on the nameplate below. As per the wiring diagram the transformer is provided with contacts for the following:
[ul]
[li]Thermometer (26Q)[/li]
[li]Liquid level (71)[/li]
[li]Pressure-Vacuum gauge (63V)[/li]
[/ul]
The Transformers are being protected by an ABB RET615 relay with included overcurrent and differential protection. The RET615 has spare input contacts that are directly connected to the tripping coil of the breaker. Would it be adequate to use the Pressure-vacuum gauge contacts as extra protection for the Transformer as well?
Your thought is highly appreciated.
Jairo
We are currently installing 4 new station transformer of 1600 kVA each as indicated on the nameplate below. As per the wiring diagram the transformer is provided with contacts for the following:
[ul]
[li]Thermometer (26Q)[/li]
[li]Liquid level (71)[/li]
[li]Pressure-Vacuum gauge (63V)[/li]
[/ul]
The Transformers are being protected by an ABB RET615 relay with included overcurrent and differential protection. The RET615 has spare input contacts that are directly connected to the tripping coil of the breaker. Would it be adequate to use the Pressure-vacuum gauge contacts as extra protection for the Transformer as well?
Your thought is highly appreciated.
Jairo