Humble2000
Electrical
- Nov 17, 2005
- 132
Dear All,
In transformer protection with fuse and LV power circuit breakers on the secondary, I understand that the maximum fuse rating on the primary has to be maximum 250% of the full load and the maximum LTP is 125% of the secondary full load. The instantaneous set up is dictated by short circuit rating at that location.
I did not find any information about any rules to how to set up (based on what criteria) the short circuit pick up and delay for the breaker. I appreciate any feedback on this.
I also noticed that IEEE uses ANSI point as another point that needs to be shown on the graph. There are multipliers which applies to this as well( 16.6 for 3.75MVA and 17.6 for 750KVA XFR). What are these numbers and what they represent? Thank you very much for any answers on the above questions.
Regards,
In transformer protection with fuse and LV power circuit breakers on the secondary, I understand that the maximum fuse rating on the primary has to be maximum 250% of the full load and the maximum LTP is 125% of the secondary full load. The instantaneous set up is dictated by short circuit rating at that location.
I did not find any information about any rules to how to set up (based on what criteria) the short circuit pick up and delay for the breaker. I appreciate any feedback on this.
I also noticed that IEEE uses ANSI point as another point that needs to be shown on the graph. There are multipliers which applies to this as well( 16.6 for 3.75MVA and 17.6 for 750KVA XFR). What are these numbers and what they represent? Thank you very much for any answers on the above questions.
Regards,