davidbeach
Electrical
- Mar 13, 2003
- 9,492
I think I've run into this more than just this once, where a wye-delta transformer is installed with the wye side H0 or X0 bushing connected to an arrestor rather than either a grounding impedance or a solid ground. For now I've got one to consider how to represent in our OneLiner model. We don't own the transformer, but it connects directly to our system with the wye side facing us; at 230kV. For the most part, modeling it as an ungrounded wye is reasonable, for most faults the arrestor doesn't conduct and the wye remains ungrounded. But for SLG faults very close to that transformer the arrestor will conduct and the transformer suddenly starts contributing ground fault current, potentially significant amounts of current.
Have others faced similar situations? How do you model it? Do you change from ungrounded for remote faults to solidly grounded for close-in faults? Do you have any good fault records to show how it really works?
Thanks.
Have others faced similar situations? How do you model it? Do you change from ungrounded for remote faults to solidly grounded for close-in faults? Do you have any good fault records to show how it really works?
Thanks.