emmjea001
Electrical
- Jul 17, 2013
- 24
Hi, I am looking for a standard or guidance note covering the need for trenches or bund walls to mitigate against oil spilage and fire risk?
The local authority here only have approved designs for substations that are externally facing, in this case I have a client owned substation which is internal to the building, and I am worried about a tank rupture and subsequent spread of oil to other parts of the building and the associated fire risk?
The local authority do not seem concerned and have said it is not required, but I think it is. So looking for some guidance or typical details?
also wondering if (aside from good practice) there is any actual requirement for separation of rooms for LV switch/ TX / MV switch - or combination thereof
Thanks
The local authority here only have approved designs for substations that are externally facing, in this case I have a client owned substation which is internal to the building, and I am worried about a tank rupture and subsequent spread of oil to other parts of the building and the associated fire risk?
The local authority do not seem concerned and have said it is not required, but I think it is. So looking for some guidance or typical details?
also wondering if (aside from good practice) there is any actual requirement for separation of rooms for LV switch/ TX / MV switch - or combination thereof
Thanks