Hey Folks,
I am laying out a small distribution transformer that will have 2 feeders... here are the specifics;
Primary phase Protection: 50A Din fuses 4160v
Transformer: 225kVA, delta grounded wye (15a) 600v secondary
Secondary phase Protection: none
Feeder 1: CH series C JD MCCB (100A trip)
Feeder 2: Sames as feeder 1
The NGR has a se-325 for GF protection and will be used to shed both feeders upon a GF occuring.
The name of the game is to keep the cost low... so we did not go with a main on the secondary.
Question:
I am running separate feeds to each feeder (only 15' max). What size do I have to make the cables to insure the primary fuses protect the cables?
In this case I will probably just size them to the secondary FLC + 125% which exceeds the breaker frame ratings anyways; but what if the feeder cables were only sized for 100A?
I am laying out a small distribution transformer that will have 2 feeders... here are the specifics;
Primary phase Protection: 50A Din fuses 4160v
Transformer: 225kVA, delta grounded wye (15a) 600v secondary
Secondary phase Protection: none
Feeder 1: CH series C JD MCCB (100A trip)
Feeder 2: Sames as feeder 1
The NGR has a se-325 for GF protection and will be used to shed both feeders upon a GF occuring.
The name of the game is to keep the cost low... so we did not go with a main on the secondary.
Question:
I am running separate feeds to each feeder (only 15' max). What size do I have to make the cables to insure the primary fuses protect the cables?
In this case I will probably just size them to the secondary FLC + 125% which exceeds the breaker frame ratings anyways; but what if the feeder cables were only sized for 100A?