confused99
Mechanical
- Sep 16, 2003
- 1
We are currently having an discussion between engineers (mechanical) about how you calculate a transformer size in kVA from the W/m2 loading figures.
i beleive that the kVA load required is a factor of total floor area, W/m2 and divided by the power factor.
a colleague of mine states that i need to divide this figure by sq rt of 3 to take account of 3 phase vector diagrams.
another colleague states that i need to divide by 3 as there will be 3 phase currents of all equal value to line current.
i beleive that power delievered/required is not dependant on the no of phase and that 3 phase system only reduce conductor size and improve the efficiency of power delivered by not delivering zero power twice in a cycle.
Clarification please?