kashew

Electrical
Jul 16, 2004
10
Can someone tell me if there is a reference that provides typical distribution transformer impedances? I'm looking for %Z and either X/R ratios or %X and %R values.

The X/R table in IEEE red book is not adequate.
 
Replies continue below

Recommended for you

This is exactly what I have been searching. I was looking through the rest of the document and have a question. Table 17 lists cable resistance and reactance in magnetic and non-magnetic conduit. Are cable resistance and reactance for direct buried cable the same as the non-magnetic conduit values? If not where can I find some values for direct buried?
Thanks

The NAVGraph document will also be useful to me since it has transformer losses. Thanks William!
 
You can think of the "non-magnetic conduit" values as being "not in magnetic conduit" values. Once the conductors are no longer enclosed in a magnetic container, what is around the conductors has much less impact on impedance than does the relative location of the conductors.
 