Is there any thumb rule to quickly estimate what should be the rated static pressure of the tank of a 132/34.5kV, 140MVA transformer, with the conservator at a height of 2.5 meter.
IEC 60076-1 states that the tank shall be tested for the pressure of at least 30 kPa over the normal liquid pressure.
By applying the above standard, the static pressure in this case is expected to be about 2.5 mtr x 0.8 = 2 bar, assuming the specific gravity of oil is 0.8. Hence the test pressure shall be
= 2 bar + 30 kPa
= 2 bar + 0.3 bar
= 2.3 bar
I would appreciate if someone from the fraternity could validate or comment on the above.