Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer TCC

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
396
0
16
NL
This is the TCC of a Transformer; both the HV side and LV side relays are plotted.

Transformer_Protection_kcskqm.png


It seems that relay settings are okay. Is there any possibility that HV relay would be tripped in any other event? If yes, under what situation?
 
Replies continue below

Recommended for you

Any possibility? Not enough information. How was the transformer inrush curve developed? What type of transformer? It looks fine in the TCC, but transformer inrush is a complicated event. If this is just a generic inrush curve generated by the software, I'd say there might be some possibility. If it trips, just increase the instantaneous pickup.
 