Transformer Theory

Status
Not open for further replies.

alc

Industrial
Oct 2, 2001
1
Would like to get some instruction on wiring a 240/110 transformer. Our shop is constantly discussing the proper grounding method for the transformer secondary. E.G.: We have 240VAC, 3PH, 3-wire coming into a breaker panel. One of the breakers feeds a 1KV 240/110 transformer. Since there are only three wires coming into the breaker panel, how is a neutral obtained on the secondary side of the transformer? And what about grounding? I know this is basic stuff, but this application exists on a trailer and it doesn't look right to me. The 240 panel has no ground bus bar. It also has a neutral bus bar but nothing is connected to it? Some transformer theory would be appreciated.

alc
 
Replies continue below

Recommended for you

I´ll try to answer your question: The most common and simple way to obtain a neutral wire on a transformer secondary is to perform a Y connection instead of a delta. The common point of a Y is a natural neutral. That neutral can be wired as well, and in most cases, when possible, it is advisable to connect it to ground.
Neutrals on both sides of a transformer are electrically independent although they are generally interconnected. You can get only a neutral on a Y connected secondary even the primary is delta connected.
There is another way to obtain a neutral when Y connection is not possible or when mains is three wires. In such a circunstances you must use an special three phase coil with zig-zag connection.
For more details let me know.

Julian
 
See "...typical transformer configurations that are used to supply 60 Hz power at 600 volts or less in the United States."

"UNGROUNDED DELTA" and "TWO-WIRE" describe the transformer configuraions you describe.
 