TimDta
Electrical
- Nov 18, 2007
- 7
With reference to transformer thermal characteristics, power system analysis software ETAP shows a short line & inrush current point(s) in protection co-ordination graphs. The transformer, built to AS60076, is 1000kVA, Dyn11, oil-immersed, Z=6%, temperature class of insulation=A, Winding temperature rise=65DegC, Top oil temperature rise=60DegC. Additional info such as Cross Sectional Area (sqmm) is not known and if required must be assumed. To validate ETAP (or even PTW, DIgSILENT) outputs, what additional assumptions need to be made & what steps/IEC equations are required to generate the transformer thermal(i.e. current vs. time) curve, inrush current point(s)?
Based on the basic 1000kVA transformer data inputs to ETAP, following are the data points:
Time(Sec) ETAP Current(Amps)
2 291.6
1.5 344.7
1 437.6
0.5 657
Based on the basic 1000kVA transformer data inputs to ETAP, following are the data points: