LBolt
Electrical
- Mar 13, 2003
- 11
We have 3 8333kva 44kv-7200V single phase transformers connected in Delta primary and Wye secondary. We had a percentage differential relay operate and a dip on our system voltage. The transformers were broken loose and a TTR test was performed on each. Two nulled the meter at ratio the correct value 6.111. The last nulled at approximately 3. The tap was changed an still measured 3. The transformer has been sent to the shop and untanked. No apparent problem and all the tap ratios are measuring very closely to the calculated values. Has anyone ever experienced anything like this?