Guys hi,
Looking for a quick and simply response to a technical issue regarding overall site power factor.
Situation. 3km of 132kv cable feeding a 56MVA transformer (132/11.5/11.5). 30 metres of 11kv cable connected to a 11kv switch panel. The load at the 11kv switchable is 3MVA. Local meter also states as pf of 0.95. However upstream (3 kms away) DNO meters are reading 0.6.a) does this sound right if so, is it down to the lightly loaded transformer.
Lastly'I had a loadflow analysis done in house which kicks out a figure of 0.95 at supply and load end! Confused.
Looking for a quick and simply response to a technical issue regarding overall site power factor.
Situation. 3km of 132kv cable feeding a 56MVA transformer (132/11.5/11.5). 30 metres of 11kv cable connected to a 11kv switch panel. The load at the 11kv switchable is 3MVA. Local meter also states as pf of 0.95. However upstream (3 kms away) DNO meters are reading 0.6.a) does this sound right if so, is it down to the lightly loaded transformer.