Transformers Grounding

Status
Not open for further replies.

zabihz

Electrical
Jan 22, 2015
1
Dear All Respected Professionals.

Power/ Distribution Transformer body Grounding and Neutral Earthing should be connected separtlty or to be connected with same earthing net?

As i did't find any specific standard.

Please Help me to find the solution.

Thanking in Advance.
Zabih Ullah Faizi.

 
Replies continue below

Recommended for you

Whether you can get away with a common HV and LV earth depends on the allowable rise of earth potential, prospective earth fault current and the impedance of the earth grid. Some Companies have rules of thumb, but there isn't a universally applicable answer.
Regards
Marmite
 
In the US, multi-grounded primary neutrals must be connected to an ground electrode at each transformer. See NEC Rule 96C.
 