This is my first post so bear with me. I've been asked to do some very preliminary research into transformer efficiency and determine if utility cost savings can be obtained by swapping out old transformers with new, "energy efficient" transformers. I am not designing a system by any means.
The facility is a 15 floor office building. The existing transformer on a typical floor is 480-208Y/120V, 150kVA, K-13 rated, and the peak demand is estimated at 60kW. The peak demand is not expected to increase.
My understanding of K rated transformers is that they are used when non-linear loads such as florescent lighting and electronics such as computers can damage a standard transformer. However, since the peak demand appears to be 50% or less of the 150kVA, I would think K-13 is overkill, and am wondering if these can be replaced with K-4 or non-K rated but energy efficient transformers.
In short, my question is how should the following variables be considered:
1)50% peak demand on a K-13 transformer - stay with K-13 but reduce transformer to 112.5 or 75kVA?
2)Stay with 150kVA but reduce to K-4 or Type EE model?
For the sake of this post, I am disregarding the demolition and replacement cost to do this, and am strictly looking at the cost savings over time given a more "efficient" transformer for this application.
Thanks for the help,
RDL
This is my first post so bear with me. I've been asked to do some very preliminary research into transformer efficiency and determine if utility cost savings can be obtained by swapping out old transformers with new, "energy efficient" transformers. I am not designing a system by any means.
The facility is a 15 floor office building. The existing transformer on a typical floor is 480-208Y/120V, 150kVA, K-13 rated, and the peak demand is estimated at 60kW. The peak demand is not expected to increase.
My understanding of K rated transformers is that they are used when non-linear loads such as florescent lighting and electronics such as computers can damage a standard transformer. However, since the peak demand appears to be 50% or less of the 150kVA, I would think K-13 is overkill, and am wondering if these can be replaced with K-4 or non-K rated but energy efficient transformers.
In short, my question is how should the following variables be considered:
1)50% peak demand on a K-13 transformer - stay with K-13 but reduce transformer to 112.5 or 75kVA?
2)Stay with 150kVA but reduce to K-4 or Type EE model?
For the sake of this post, I am disregarding the demolition and replacement cost to do this, and am strictly looking at the cost savings over time given a more "efficient" transformer for this application.
Thanks for the help,