Transmition lost in Kw/m

Status
Not open for further replies.

CARLOSMT

Electrical
Joined
Jan 21, 2004
Messages
1
Location
US
Is the first time, i have to desing a transmition line so? I need a formula to calculete the lost of power in 11 Km transmition line in double circuit for 34.5 KV with a power of 15 Mw per circuit, i have a current of 753.06 ampers with a ACSR conductor.

Carlos Manuel Tam Gonzalez
 
sounds like a home work assignment...this is too basic a question to ask if you are assigned to design a tranmission line.

Ask your senior engineers..

Hint: kw loss= I^2*R. Calculate values per phase. Multiply by three for the total 3 phase loss. Refer to some basic text books, hand books etc.

There other more serious things to consider in tranmission line design. An when it is overhead line, like urs, mechanical, sturctural and civil engineering plays much greater role than electrical.
 