First of all 200 A it is the ampacity of this cable in free air 45oC ambient 85oC conductor maximum temperature.
The cable will be cooled by the equipment connected at both ends.
Cable is PVC insulated, copper conductor [flexible] 90oC- maximum permissible.
According to:
Siemens-Power Cables and Their Applications by Lothar Heinhold
ch.18.6.1 up to ch.18.6.5.
DT= (TCr-Ta)*(1-exp(-t/tau) eq. 18.113
Where:
DT=conductor temperature rise [oC]; TCr=90oC max.permissible conductor temperature;Ta=air temperature. tau=time constant[SEC]
tau=T*C 18.114 or finally tau=B*(q/Ir)^2
From Table 18.38 for copper conductor 90oC B=9.09*10^15 [A^2*sec/m^4]
q=50/10^6 m^2 conductor cross section area. Ir=280 A
tau=9.09*10^3*(50/280)^2=290 sec
DT= (90-45)*(1-exp (-90/290)) =12 oC
The conductor temperature will be= 45+12= 57 oC
If the second start will be after 4 hours the conductor will be at ambient temperature.
According to:
EPRI POWER PLANT ELECTRICAL REFERENCE SERIES VOL.4 WIRE AND CABLES
Tc(t)=Tc(0)+[Tc(f)-Tc(0)]*(1-exp(-t/K) Eq.4-23
Tc(f)=(Ic/IA)^2*(Tc-TA)+TA
Ic=280 A; IA=200 A ;TA=45;Tc=85;Tc(0)=TA[starting from ambient]; K=tau=290 sec
Tc(f)=(280/200)^2*(85-45)+45=123.4 o C.
Tc(90 sec)=45+(123.4-45)*(1-exp(-90/290))=65.9 oC
No problem at all.