In the Canadian code, Tables 36A and 36B give the ampacitys for different sizes and configurations of Neutral supported cables.
The tables list three configurations:
Duplex,
Triplex,
and
Quadruplex.
Neutral supported cable is used overhead in free air.
Comparison, aluminum conductors:
Table 36A #2 Triplex NS 75,- 140 Amps
Table 3 #2 RW75 single conductors in free air,- 135 Amps.
(Based on the 2006 CEC, my copy of the 2015 CEC is at another location.)
Three conductor cables are generally suitable for installation in conduit. Some are suitable for wet locations, some are suitable for direct burial.
Triplex is a configuration of neutral supported cable that is always used overhead in free air and is common for service drops.
Texcan refers to it as Triplex Utility Distribution Cable.