tripping time of Current limiting circuit breakers and fuses 2

Status
Not open for further replies.

victa1288

Electrical
Apr 18, 2006
48
I am working on International project based on IEC standards. But I don't have data for tripping times of Current limiting circuit breakers and fuses.

Some people said it is 1/2 cycle. Other people said it is 1/4 cycle.

I would apprecite it if anybody here can provide me more acurate infomation.
 
Replies continue below

Recommended for you

It can only be current limiting if the interrupting time is less than 1/2 cycle. At exactly 1/2 cycle there is no limitation, at just under 1/2 cycle there isn't much limiting. The greatest amount of limiting will happen with interrupting times around 1/4 cycle. The exact time will depend on the magnitude of the fault current and the characteristics of the device.
 
I agree with David - it has to be faster than 1/2 cycle to be current-limiting - but remember - it isn't always going to be current limiting - that depends on the current magnitude. If you look at the fuse curve and based on your fault current the clearing time is 2 cycles, there is no guarantee of current-limiting.
 