We have a ground indication on an ungrounded single-phase 120v system supplied by an inverter, feeding numerous electronic loads.
We measured from each leg to ground and found 85vdc on one leg and 45vdc on other leg. (total voltage 130vdc)
With a single-phase system there is no possibility for unbalance. With no known loads connected to ground there should be balanced voltage from each leg to ground, based on similar physical configuration (capacitance) from each phase to ground.
We don't think our electonic equipment has any caps connected to ground.
The loads cannot be removed for ground isolation. Any suggestions for troubleshooting. Our plan is:
Check another similar system to confirm these measured voltages are in fact abnormal.
Attempt to measure equipment grounding conductors by clamp-on.... or attempt to measure both supply conductors with one clamp-on. This may help us to isolate the suspect load or component.
We measured from each leg to ground and found 85vdc on one leg and 45vdc on other leg. (total voltage 130vdc)
With a single-phase system there is no possibility for unbalance. With no known loads connected to ground there should be balanced voltage from each leg to ground, based on similar physical configuration (capacitance) from each phase to ground.
We don't think our electonic equipment has any caps connected to ground.
The loads cannot be removed for ground isolation. Any suggestions for troubleshooting. Our plan is:
Check another similar system to confirm these measured voltages are in fact abnormal.
Attempt to measure equipment grounding conductors by clamp-on.... or attempt to measure both supply conductors with one clamp-on. This may help us to isolate the suspect load or component.