tulum
Industrial
- Jan 13, 2004
- 335
I have already asked the question to Schneider Product Specialists in the states and have not received much help.
Here is my situation,
I have a system with a transformer that provides approximately 18-20kA of fault current. What is proposed is to have a Cutler Hammer ND main breaker on the secondary that is good for 25kA - This is fine.
The problem is that on the load side of the main breaker it is proposed to put a couple Squared combination starters size 2, size 4, and size 5.
Note - the components are Squared but the manufacturing has been farmed out to a local panel builder - i.e. not in squared enclosures.
Here is a breakdown:
Size 2: Mag-Gard (FAL3605016MV) 50A MCP, with Squared Size 2 starter (8536SDO1V02H20S) and O/L's
Size 4: Mag-Gard (KAL3625025MV) 250A MCP, with Squared Size 4 starter (8536SFO1V02H20S) and O/L's
Size 5: Mag-Gard (LAL3640032MV) 400A MCP, with Squared Size 5 starter (856SGO1V02H20S) and O/L's
The MPC's do not come with an interrupting rating alone - as per UL requirements. However, they do have come with a combination rating when used in combination with appropriate motor starters.
The sticker ratings that were shipped loose with the above are all 10kA. However, these ratings all seemed to be based on being tested within certain Squared enclosures as a combination (as per UL 508), i.e. in a squareD standard enclosure a size 4 is 22kA and in a Nema 7-9 enclosure it is 10kA. This seems to be more of an indication of the amount circuit current a enclosure can contain without deforming, rather than component classification.
My question is:
I want to know if the above starter COMPONENTS are suitable for use on a system that can supply 20kA fault current, i.e. enclosure not accounted for. My gut is this is a bad setup all together, and the spec should have included fused disconnects.
Regards,
TULUM
Here is my situation,
I have a system with a transformer that provides approximately 18-20kA of fault current. What is proposed is to have a Cutler Hammer ND main breaker on the secondary that is good for 25kA - This is fine.
The problem is that on the load side of the main breaker it is proposed to put a couple Squared combination starters size 2, size 4, and size 5.
Note - the components are Squared but the manufacturing has been farmed out to a local panel builder - i.e. not in squared enclosures.
Here is a breakdown:
Size 2: Mag-Gard (FAL3605016MV) 50A MCP, with Squared Size 2 starter (8536SDO1V02H20S) and O/L's
Size 4: Mag-Gard (KAL3625025MV) 250A MCP, with Squared Size 4 starter (8536SFO1V02H20S) and O/L's
Size 5: Mag-Gard (LAL3640032MV) 400A MCP, with Squared Size 5 starter (856SGO1V02H20S) and O/L's
The MPC's do not come with an interrupting rating alone - as per UL requirements. However, they do have come with a combination rating when used in combination with appropriate motor starters.
The sticker ratings that were shipped loose with the above are all 10kA. However, these ratings all seemed to be based on being tested within certain Squared enclosures as a combination (as per UL 508), i.e. in a squareD standard enclosure a size 4 is 22kA and in a Nema 7-9 enclosure it is 10kA. This seems to be more of an indication of the amount circuit current a enclosure can contain without deforming, rather than component classification.
My question is:
I want to know if the above starter COMPONENTS are suitable for use on a system that can supply 20kA fault current, i.e. enclosure not accounted for. My gut is this is a bad setup all together, and the spec should have included fused disconnects.
Regards,
TULUM