marada93
Electrical
- Nov 15, 2003
- 38
Some time ago I had posted concerning the potential benefit to operation our steam turbine with valves wide open. As it turns out, I have had the opportunity to run in this mode, so I need to bounce some numbers back to you guys who pushed me in the right direction before...so heres what I've got.
Just as a reminder, my turbine has four control valves that operate sequentially with an inlet steam condition. The turbine is rated for 68.9 MW, with design inlet steam conditions of 1450 psig and 950 F. Our dispatched full load output is only 58 MW. At 58 MW, CVs 1&2 would be approximately 60%, with CV 3 at about 15%.
Recently (last week) I was given the opportunity to go valves wide open on the turbine to evaluate performance and efficiency. Now, I'm able to make the 58 MW output with inlet steam conditions at 1325 psig / 950 F with all four control valves wide open. MW load is being controleed by the Plant Master, which directly controls the firing rate on two boilers. Overall plant operation has been exceptional, although it was exceptional before as well.
That being said, it seems to me that if I'm making full load with 1325 psig, whereas before I was using 1450 psig, then I was taking a 125 psig pressure drop across the three throttled CVs.
It seems like since this is the case, we're better off running VWO for a number of reasons, such as:
1- Lower pressure on the boilers and related piping by the same 125 psig.
2- Less wear on the turbine valve plugs and seats.
3- Feed pumps deliver water to the boilers much easier at reduced pressure (lower auxiliary power requirements
4- Silica carryover is less of a factor at reduced pressure.
5-Enthalpy of the steam is slightly increased at the lower pressure (1465.6 BTU/lb vs. 1461.2 BTU/lb at 1450 psig)
Does the increased BTUs correspond directly to an equvalent BTU input to the boilers? Seems like it should, even though it's slight.
What else am I missing? Any and all input is greatly appreciated byrdj and poetix gave me alot of useful iinfo last time. You guys still out there?
Thanks in advance!
Just as a reminder, my turbine has four control valves that operate sequentially with an inlet steam condition. The turbine is rated for 68.9 MW, with design inlet steam conditions of 1450 psig and 950 F. Our dispatched full load output is only 58 MW. At 58 MW, CVs 1&2 would be approximately 60%, with CV 3 at about 15%.
Recently (last week) I was given the opportunity to go valves wide open on the turbine to evaluate performance and efficiency. Now, I'm able to make the 58 MW output with inlet steam conditions at 1325 psig / 950 F with all four control valves wide open. MW load is being controleed by the Plant Master, which directly controls the firing rate on two boilers. Overall plant operation has been exceptional, although it was exceptional before as well.
That being said, it seems to me that if I'm making full load with 1325 psig, whereas before I was using 1450 psig, then I was taking a 125 psig pressure drop across the three throttled CVs.
It seems like since this is the case, we're better off running VWO for a number of reasons, such as:
1- Lower pressure on the boilers and related piping by the same 125 psig.
2- Less wear on the turbine valve plugs and seats.
3- Feed pumps deliver water to the boilers much easier at reduced pressure (lower auxiliary power requirements
4- Silica carryover is less of a factor at reduced pressure.
5-Enthalpy of the steam is slightly increased at the lower pressure (1465.6 BTU/lb vs. 1461.2 BTU/lb at 1450 psig)
Does the increased BTUs correspond directly to an equvalent BTU input to the boilers? Seems like it should, even though it's slight.
What else am I missing? Any and all input is greatly appreciated byrdj and poetix gave me alot of useful iinfo last time. You guys still out there?
Thanks in advance!