No IRstuff, a 3-phase full-wave rectifier requires 6 diodes in total, 2 per phase.
Does the alternator have 6 leads coming out of the stator? I expect it has two 3-phase windings shifted 30 degrees, at least I think 30 degrees would be used here. That makes DC with twice as many pulses per cycle which reduces the output ripple, reduces the harmonics and most likely increases the current capability.
It might use 60 degrees shift, I'm not sure off hand. The 30 degrees shift is simple to get with a transformer because that is the wye to delta shift angle so it gets used with 12-pulse rectifiers.
Look up 12-pulse rectifiers for more info, it's the same basic principle.