Rinku12
Structural
- Jul 6, 2021
- 5
hi ,
The issue is a step in the monorail beam flange. The step is about 3/16" and is due to I-beam twist from the mill but its within code tolerance. See attached picture.
The hoists are going to pass over the joint with misalignment. The track running surface vertical misalignment limit is virtually zero ( as close as possible) in more restrictive codes ( CMAA ) and max 1mm in less restrictive codes (ANSI – MH27.1) .
We need to realign the surfaces to achieve the tolerances. My suggestion for the adjustment is to align them as closely as possible considering the limitations we have and then grind smooth the transition. Its a joint so I don't flexure stress due to bending in addition to local stress by wheel load. I checked this beam by CMAA SPEC 74.
I would appreciate expert opinion here.
The issue is a step in the monorail beam flange. The step is about 3/16" and is due to I-beam twist from the mill but its within code tolerance. See attached picture.
The hoists are going to pass over the joint with misalignment. The track running surface vertical misalignment limit is virtually zero ( as close as possible) in more restrictive codes ( CMAA ) and max 1mm in less restrictive codes (ANSI – MH27.1) .
We need to realign the surfaces to achieve the tolerances. My suggestion for the adjustment is to align them as closely as possible considering the limitations we have and then grind smooth the transition. Its a joint so I don't flexure stress due to bending in addition to local stress by wheel load. I checked this beam by CMAA SPEC 74.
I would appreciate expert opinion here.