electricpete
Electrical
- May 4, 2001
- 16,774
I have a motor with oscillating current on in-line panel ammeter and worsening trend in apparent pole pass sidebands around 60hz in current.
In attempting to rule out process oscillation as the cause, I have verified no movement of refrigerant control valve linkages, but I'd like to get more confidence using the two-ammeter method as descirbed on page 7 here:
Page 7 talks about the two ammeter method.
Basically this method checks whether the (envelope of the) oscillation is in-phase among phases. (in-phase indicates simple load oscillation, rotating phase indicates rotor defect as bar bar passes among phases at pole pass frequency).
It is suggested to use two identical analogue ammeters.
The motor is in-service. Access to tag it out is limited. It is possible we have provisions to short ct secondary and insert extra meters in-line with motor running but we'd prefer not to do that if not necessary.
I'm wondering if we can expect reasonable results on the two ammeter test using analog clamp-on ammeters vs analogue in-line ammeters.
In absence of any advice, we will probably end up trying it to see what the results "look like". But even that non-intrusive clamp-on check will be harder for us than you might think. Would prefer not to mobilize the team for a first clamp-on check that doesn't work and then have to ask for a second check using in-line meters. So I'm still very interested to hear thoughts/predictions about what we can expect with that clampon test method.
More details on the particular case here are attached. Also discussed at another forum:
Attachment doesn't seem to be sticking here... I'm not sure why.
=====================================
(2B)+(2B)' ?
In attempting to rule out process oscillation as the cause, I have verified no movement of refrigerant control valve linkages, but I'd like to get more confidence using the two-ammeter method as descirbed on page 7 here:
Page 7 talks about the two ammeter method.
Basically this method checks whether the (envelope of the) oscillation is in-phase among phases. (in-phase indicates simple load oscillation, rotating phase indicates rotor defect as bar bar passes among phases at pole pass frequency).
It is suggested to use two identical analogue ammeters.
The motor is in-service. Access to tag it out is limited. It is possible we have provisions to short ct secondary and insert extra meters in-line with motor running but we'd prefer not to do that if not necessary.
I'm wondering if we can expect reasonable results on the two ammeter test using analog clamp-on ammeters vs analogue in-line ammeters.
In absence of any advice, we will probably end up trying it to see what the results "look like". But even that non-intrusive clamp-on check will be harder for us than you might think. Would prefer not to mobilize the team for a first clamp-on check that doesn't work and then have to ask for a second check using in-line meters. So I'm still very interested to hear thoughts/predictions about what we can expect with that clampon test method.
More details on the particular case here are attached. Also discussed at another forum:
http://www.maintenance.org/topic/cast-rotor-worsening-current-signature-trend-no-change-in-vibration
Attachment doesn't seem to be sticking here... I'm not sure why.
=====================================
(2B)+(2B)' ?