Two instrumemts, Same Loop

EEENGRX

Electrical
Sep 11, 2021
70
I have an existing Radar Level transmitter on a Tank with a HART protocol. I want to hook up a pressure transmitter to same tank but on the already existing loop. what is the best way to run thisn connection as i think thisnis possible since they have same HART protocol.I need very clear ways to run this wiring.
 
Replies continue below

Recommended for you

Two approaches, either of which will make the cost of running another STP cable out the to the tank look cheap, by comparison.

- HART multidrop: Uses HART enabled AI card with pass through to pass the hart signals through to your asset management software.

- HART multiplexor: A HART mux switches from one HART device to another and maps the data it gets to registers in the mux. The registers are typically accessible via a Modbus/TPC server that your control system then reads the data from.

A 2nd cable is dirt bag simple in comparison. It's just 4-20mA, leave the HART alone.
 