An incorrect switching order was issued by dispatch that would have left two 50 MVA LTC Transformers tied together through the 13.8 kv bus tie switch. Fortunately the field techs caught the error before carrying out the order.
They were speculating about the damage that this could cause if the LTCs began to buck and boost and went to 16 lower and 16 raise.
The XFMRs are 115000Delta/13800Wye and high sides are connected to the same high line. Low sides go through 2000 amp Main VCBs then to distribution buses with five 1200 amp Feeder VCBs on each bus
The load is low this time of year so I don’t think overloading one LTC is an immediate problem. And I know that opening the bus tie switch would cause severe arcing.
I know there would be a lot of circulating current between the LTCs. What problems can this circulating current cause during low load season?
What problems could you have during peak load season? Worst case scenarios please.
Thanks in advance.
They were speculating about the damage that this could cause if the LTCs began to buck and boost and went to 16 lower and 16 raise.
The XFMRs are 115000Delta/13800Wye and high sides are connected to the same high line. Low sides go through 2000 amp Main VCBs then to distribution buses with five 1200 amp Feeder VCBs on each bus
The load is low this time of year so I don’t think overloading one LTC is an immediate problem. And I know that opening the bus tie switch would cause severe arcing.
I know there would be a lot of circulating current between the LTCs. What problems can this circulating current cause during low load season?
What problems could you have during peak load season? Worst case scenarios please.
Thanks in advance.