emadmoad
Electrical
- Mar 17, 2005
- 7
situation is as following :
I have one generator wich supports all the plant loads 24 hours.
one of the loads is a concrete mixer which is driven using 2 motors ,37KW each.
These 2 motors are started using one star delta circuit(3 contactors) and it is made by the manufacturer.
the plant is working OK for 3 years untill now , but nearly every day at night and only at night upon starting these 2 motors the plant lights are completely shut down and I think the generator is interrupted for 1 or 2 seconds then it works normally !!!!(but it does not stop)
MY question is : IS THIS INTERRUPTION A SORT OF VOLTAGE DROP DUE TO MOTORS STARTING ???
HOW CAN I ELLIMINATE IT ?
ANOTHER QUESTION : IF I MADE EACH MOTOR STARTS USING ONE SEPARATED STAR DELTA ( 3 CONTACTORS STAR DELTA FOR EACH MOTOR) DOES THIS REDUCE THE STARTING CURRENT LESS THAN IF THE TWO MOTORS ARE STARTED USING ONE STAR DELTA CIRCUIT ??
thanks
I have one generator wich supports all the plant loads 24 hours.
one of the loads is a concrete mixer which is driven using 2 motors ,37KW each.
These 2 motors are started using one star delta circuit(3 contactors) and it is made by the manufacturer.
the plant is working OK for 3 years untill now , but nearly every day at night and only at night upon starting these 2 motors the plant lights are completely shut down and I think the generator is interrupted for 1 or 2 seconds then it works normally !!!!(but it does not stop)
MY question is : IS THIS INTERRUPTION A SORT OF VOLTAGE DROP DUE TO MOTORS STARTING ???
HOW CAN I ELLIMINATE IT ?
ANOTHER QUESTION : IF I MADE EACH MOTOR STARTS USING ONE SEPARATED STAR DELTA ( 3 CONTACTORS STAR DELTA FOR EACH MOTOR) DOES THIS REDUCE THE STARTING CURRENT LESS THAN IF THE TWO MOTORS ARE STARTED USING ONE STAR DELTA CIRCUIT ??
thanks