Hi all. In my company's shop we have an ABB two speed motor for repair, two seperate windings in the same stator - 6 pole and 8 pole, both Delta connected. It was badly burnt so re-wound but now we have the following problem:
The 8 pole machine runs fine no load - expected no-load current of 26%. Then we connect to the 6 poles.
The 6 pole machine draws approx rated current in two phases and higher in the third.
We are using a VFD for the tests but we did perform one off DOL start of the 6 pole machine and same 'bad' result.
Plenty of electrical checks and reworking polarities etc etc so we know the 6 pole and 8 pole windings have not been internally connected. The surge test results of the 6 pole connections showed a problem until we opened the 8 pole windings.
We opened the 8 pole delta connections and the 6 pole motor runs fine. So there seems to be some interaction between the windings causing the 6 pole machine to behave this way.
We rewound again (just in case) but did the 6 pole machine first, performed a surge test to check it was ok. Then we installed the 8 pole windings and we get the 'bad' surge test results in the 6 pole machine again - ie one phase different to the other two.
So we are expecting to run the 6 pole machine and get the high current again.
The motor terminal box doesn't have links to open the 8 pole windings if we want to run the 6 pole machine.
ABB won't supply the motor winding schematic. The motor nameplates are attached.
Any ideas anyone?
The 8 pole machine runs fine no load - expected no-load current of 26%. Then we connect to the 6 poles.
The 6 pole machine draws approx rated current in two phases and higher in the third.
We are using a VFD for the tests but we did perform one off DOL start of the 6 pole machine and same 'bad' result.
Plenty of electrical checks and reworking polarities etc etc so we know the 6 pole and 8 pole windings have not been internally connected. The surge test results of the 6 pole connections showed a problem until we opened the 8 pole windings.
We opened the 8 pole delta connections and the 6 pole motor runs fine. So there seems to be some interaction between the windings causing the 6 pole machine to behave this way.
We rewound again (just in case) but did the 6 pole machine first, performed a surge test to check it was ok. Then we installed the 8 pole windings and we get the 'bad' surge test results in the 6 pole machine again - ie one phase different to the other two.
So we are expecting to run the 6 pole machine and get the high current again.
The motor terminal box doesn't have links to open the 8 pole windings if we want to run the 6 pole machine.
ABB won't supply the motor winding schematic. The motor nameplates are attached.
Any ideas anyone?