TYPE E Self Protected Motor Controller

Status
Not open for further replies.

robbm

Electrical
Nov 2, 2005
56
i normally use contactors and motor circuit protectors together to form a self protected motor controller (so as to follow UL508A and eliminate the need for additional fuse protection). i've also seen this listed as a 'TYPE E' motor controller...does a type e motor controller mean strictly that it is self protected or is the definition more broad? (somewhere that has an actual defintion of a type e controller would be great)
 
Replies continue below

Recommended for you

I just had a guy from WEG in here for a dog and pony show on their control line including Type E and Type F offerings (They bought the old AEG line and now produce it themselves) here is the breakout:

A - Type A combination motor controller consisting of a disconnect switch, fuses, motor controller and overload relay

C - Type C combination motor controller consisting of Inverse time circuit breaker, motor controller and overload relay

D - Type D combination motor controller consisting of instantaneous trip circuit breaker, motor controller and overload relay

E - Type E (self-protected) combination motor controller consisting of manual self-protected combination motor controller and motor controller

F - Type F combination motor controller consisting of manual self-protected combination motor controller and motor controller
 
To add on to the above, I think you are bouncing between the Type F and Type E. The key difference is the E has to be able to identify the trip as either Overload or Short Circuit.
 
Who / what is the source for these "types"? IEC, NEC, NEMA?

JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> faq731-376
 
UL508 is correct. The UL Type E also means that the build up of parts (manual motor protector, contactor, OL and Short Circuit signaling block etc) have all been tested and certified per UL to be self-protected. A type F build up might be exactly the same as a Type E but it is not tested and certified by UL to be self-protected so I guess the simple answer is only a Type E per UL508 is truely self-protected.
 