rockman7892
Electrical
- Apr 7, 2008
- 1,172
For all of the MV 4.16kV motors in our plant we use Simens draw out contactors for the means of motor starting. This motor starter consists of the draw-out contactor with vaccum bottle contacts, Type R motor fuses on the primary of the contactor, and a motor protection relay (Multilin 269) for motor overload protection.
I have been focusing lately on fuse selection for these type R fuses. Typically I follow the Siemens application guide which reccomends a type R fuse size based upon the FLA, LRC, and acceleration time of the motor. These values usually lead directly to a fuse size to use in this starting arrangement.
From everything that I have read these fuses are stricly for short circuit protection of the circuit. We do not use the instantaneous settings on the motor relay based upon the fact that the contacors are only rated for interrupting up to a certain fault current. So from a TCC plot standpoint we let the fuse take over at the bottom of the realy curve to interrupt any fault current.
As I look at the TCC I notice that the only thing that the fuses are protecting to the right of the curve are the cables to the motor. With that being said I have wondered what the negative effect would be for selecting/using a fuse that is a higher rating than what the application guide reccomends. If for theoretically some reason we were in a pinch and did not have the correct fuse size and only had a larger size avaliable what would be the risk of using this larger fuse size since it is only used for short circuit protection, and this fuse still fell to the left of the cable damage curves?
I know the negative effects of using a type R fuse that is too small b/c I have blown several of them in the past but am curious what is being risked by using ones that are too big since the relay provides the overload protection.