DaveAtkins

Structural
Apr 15, 2002
2,888
I am working on a project where anchor bolt projection is a critical dimension. These are on grade bus stop platforms, where the custom designed shelter (designed by me, not an off the shelf shelter) will be anchored to a mat footing on grade, after which a topping slab containing a snow melt system will be placed over the mat footing.

I have instructed the design team we need a 6" topping slab, based on 4" anchor bolt projection at the shelter column base plates, and 2" cover over the anchor bolt tip. I believe 4" is a typical anchor bolt projection, but have been unable to find confirmation online. I plan to use 1-1/2" grout, and estimate the base plate will be no more than 1" thick (haven't designed them yet).

Is 4" a reasonable dimension for anchor bolt projection?

DaveAtkins
 
Replies continue below

Recommended for you

See no reason why that wouldn't work. 1 1/2" of threads above the baseplate. You could reduce 1/2" if you wanted but give a little less margin for install error.
 

This is copy and paste from PIP STE05121 Anchor Bolt Design Guide ;

( Anchor bolts should project a minimum of two threads above the fully engaged nut(s).)

Typical for Single Nuts , Projection = grout thick + base plate thick.+ 2.0 X anchor bolt dia.

 
As HTURKAK noted, it will depend on the height of the nut, which is a function of the anchor bolt diameter and the type of nut(s).

Rod Smith, P.E., The artist formerly known as HotRod10
 
A couple of cautions... make sure your anchorrods are weldable and check to see that your grout can be used to 1-1/2" thickness... 1-1/2" grout seems a little thick.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?

-Dik
 
I'd say that 4" is perfect as a minimum for 3/4" bolt and washer with 1/2" vertical placement tolerance.
 