Typical Deisel Generator Oil Storage Systems 1

Status
Not open for further replies.

JackofallMech

Mechanical
Jun 7, 2007
20
I am having a tough time rounding up info. on how to best approach designing a Deisel Oil Generator Storage system. I have 2 larg storage tanks needed for a 3 day supply that will feed 5 day tanks each feeding a gen-set. The gen-set needs 500 l/hr. I have selected the tanks and generator but have not determined the pipe size or the pump size yet. I think the day tanks will be batch filled, but I haven't decided on a rate of filling. I concerned with the system going from the storage tanks to the day tanks. Does anyone have any suggestions as to some of the particulars that I will need to concider for this system?
 
Replies continue below

Recommended for you

On yachts, the transfer pumps are large enough so that you don't spend all day just filling the day tank.

They are also often set up so they can be run continuously to 'polish' the fuel in any tank, running it through a water separator and filter and back to the tank, to remove the junk from a bad batch of fuel.

Beyond that, I know nothing.





Mike Halloran
Pembroke Pines, FL, USA
 
You didn't say the size of the day tanks, I'm guessing 1000 liters.

Look at how many hours you want to spend filling up all the day tanks (from zero), while all gen sets are running. That will give you the minimum pump rate.

So, (pump_rate - 500 l/hr)* pump_hrs = 40000
4000/pump_hrs = pump_rate - 500 l/hr
pump_rate = 4000/pump_hrs + 500

Say 1/2 a shift = 4 hours,

pump_rate = 4000L/4hrs + 500L/h = 1500L/hr

Note, as you increase the hours needed to fill, the flowrate drops by a power function approximating
(4000+500)^(4000-500)/(4000+500)

If you plot that and draw the tangets, you get a rough intersection at 2000 L/h, which I always thought was a reasonable (optimum?) max. So somewhere between 1500 and 2000.

Size the line for 2 m/s velocity.



 
We generally use the same pump that is used to fill the main tanks from a tanker, to fill day tanks also. Like BigInch suggested, the capacity of day tanks is an important variable. We have a limitation of 1000 liters for diesel here. If you don't have such limitations and if you size it for 1 shift operation then the total capacity is 20cu.mtr.

We design our main pumps to empty the tanker in maximum 1 hour and thus it is 12cu.mtr/hr. If you go with that capacity and start pumping into day tanks when the level is 1000 liters then you require about one and half hour.

It doesn't matter much, with respect to total power consumption, whether you take a small pump and run for many hours or take a big pump and run for lesser hours.

 
Thanks guys

BigInch

The head engineers here are insisting that I use double walled piping. They are super concerned with spilage. Do you have any extra comments regarding this. I'm not sure that I mentioned that this system is for a Mine. I don't know if that makes much difference but I just thought I would mention it.
 
Pipeline operators will never agree that full casing is needed. There is simply too many problems with cathodic shorting, humidity, corrosion and inspection of pipe inside casings. The biggest factor of danger for pipelines is acutally damage by third parties installing utilities in the area. Perhaps they are thinking about that factor, but it is something that can be easily handled by good marking, or laying in a trench with red colored concrete sloop poured in the top layer of backfill. I can't agree with their assessment, if it is based on corrosion leakage alone. Besides leaking diesel isn't the same thing as leaking gasoline. I've worked 10 years on large underground storage plants for gasoline, diesel and jet fuels and we did not have a single double walled or cased pipe at any of the sites.

I would be much more concerned about spillages in the storage tank area. Otherwise its just a matter of keeping excavation or other machinery away from the line in some effective manner.

 