Sep 2, 2004 #1 bahram Electrical Joined May 26, 2001 Messages 11 Location IR Can any one tell me the typical value of Xd of an AC hydro-generator with the following data: 750RPM, 1.7MW, PF=0.9,6.3kV Generally I want to know the criteria for selection of Xd or in other words teh SCR of the AC generators?
Can any one tell me the typical value of Xd of an AC hydro-generator with the following data: 750RPM, 1.7MW, PF=0.9,6.3kV Generally I want to know the criteria for selection of Xd or in other words teh SCR of the AC generators?
Sep 2, 2004 #2 mersin33 Electrical Joined Oct 11, 2002 Messages 53 Location CA you can use: Xd-synch: Avg: 1.25 Range: 0.6-1.5 Xd-transient: Avg: 0.3 Range: 0.2-0.5 Xd-subtransient: Avg: 0.2 Range: 0.13-0.32 (with dampers) Xd-subtransient: Avg: 0.3 Range: 0.2-0.5 (without dampers) All in p.u. in rated kVA base. Upvote 0 Downvote
you can use: Xd-synch: Avg: 1.25 Range: 0.6-1.5 Xd-transient: Avg: 0.3 Range: 0.2-0.5 Xd-subtransient: Avg: 0.2 Range: 0.13-0.32 (with dampers) Xd-subtransient: Avg: 0.3 Range: 0.2-0.5 (without dampers) All in p.u. in rated kVA base.
Sep 2, 2004 #3 cuky2000 Electrical Joined Aug 18, 2001 Messages 2,135 Location DO Typical reactance of hydro-gen are: a-Without damper winding……………..16 (16-50)% b-With damper wedges …………………20(13-32)% Upvote 0 Downvote
Typical reactance of hydro-gen are: a-Without damper winding……………..16 (16-50)% b-With damper wedges …………………20(13-32)%