EngineerofSteel
Structural
- May 18, 2005
- 156
I am designing the second phase of a pipe-column (or "pole barn"), shade structure. All footings are cylindrical pier footings with #3 hoops holding (8) #5 bars vertically. the #5 bars are placed 3" from the outside of the 48" diameter pier footing.
The reviewer is requesting I "check concrete footings for minimum reinforcing per U.B.C. sections 1907.12.2.1 and 1910.5.1."
the x-section area is 1810 in^2. *.0018 = 3.26 in^2 required. my (8)#5 bars provide 2.45 in^2.
The 8.625 O.D. XS pipe has an area of 12.80 in^2 and this column extends to within 3" of the bottom of the footing.
How can I justify the existing reinforcement? This is a U-3, "occupied agricultural" building.
Can I include the area of the steel in the column as part of my "reinforcement"?
Any suggestions?
-DD
The reviewer is requesting I "check concrete footings for minimum reinforcing per U.B.C. sections 1907.12.2.1 and 1910.5.1."
the x-section area is 1810 in^2. *.0018 = 3.26 in^2 required. my (8)#5 bars provide 2.45 in^2.
The 8.625 O.D. XS pipe has an area of 12.80 in^2 and this column extends to within 3" of the bottom of the footing.
How can I justify the existing reinforcement? This is a U-3, "occupied agricultural" building.
Can I include the area of the steel in the column as part of my "reinforcement"?
Any suggestions?
-DD