Colinjohnson
Electrical
- Jul 11, 2004
- 22
Hello,
I am designing a power system which comprises a 11/0.4kV 1000kVA grid connected transformer feeding an LV switchboard. In addition a 1000kVA generator will be used in parallel with the transformer for occaisional peak lopping (TRIAD operation). To meet the requirements of G59 and in order to avoid circulating currents I am proposing to operate the generator neutral earthing breaker as follows :
When the generator is started the NEB will close and the generator will run up to speed and synchronise but at the moment of synchronism the NEB will open leaving the grid transformer to carry the system neutral. Because the supply agreement if for occaisional paralleling only when the generator is carrying the entire load the grid transformer ACB will open and the generator NEB will close (Island operation).
The problem is in my office the opinion of my colleugues is that the generator neutral should be solidly bolted to earth at all times which would mean that two neutrals would be in circuit when the generator is in parallel.
Am I right and what technical arguments could I advance to win my case ?
I am designing a power system which comprises a 11/0.4kV 1000kVA grid connected transformer feeding an LV switchboard. In addition a 1000kVA generator will be used in parallel with the transformer for occaisional peak lopping (TRIAD operation). To meet the requirements of G59 and in order to avoid circulating currents I am proposing to operate the generator neutral earthing breaker as follows :
When the generator is started the NEB will close and the generator will run up to speed and synchronise but at the moment of synchronism the NEB will open leaving the grid transformer to carry the system neutral. Because the supply agreement if for occaisional paralleling only when the generator is carrying the entire load the grid transformer ACB will open and the generator NEB will close (Island operation).
The problem is in my office the opinion of my colleugues is that the generator neutral should be solidly bolted to earth at all times which would mean that two neutrals would be in circuit when the generator is in parallel.
Am I right and what technical arguments could I advance to win my case ?